SEU PVC sleeve

Status
Not open for further replies.

Jhallelec

Member
Location
Connecticut
Occupation
Electrical
Has anyone ever been failed for installing a 4/0 SEU cable in a 2” pvc from meter to a LB as a stub into the house and converted over with a FA connector.
 

HEYDOG

Senior Member
Has anyone ever been failed for installing a 4/0 SEU cable in a 2” pvc from meter to a LB as a stub into the house and converted over with a FA connector.
Just guessing…but I am thinking that one of the issues maybe that the 2” LB is not big enough for the 4/0 SEU. Also there may be an listing issue for converting from the FA to a SEU Cable connector.
 
Just guessing…but I am thinking that one of the issues maybe that the 2” LB is not big enough for the 4/0 SEU. Also there may be an listing issue for converting from the FA to a SEU Cable connector.
I doubt there are any instructions or listing documents prohibiting threading a camp connector into an FA, but one could argue that the Connector needs to bonded and is not.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The issue is usually that the 5X SE cable minimum radius of the bend in the LB cannot be maintained. An elbow in lieu of the LB solves that problem.
 

jap

Senior Member
Occupation
Electrician
The issue is usually that the 5X SE cable minimum radius of the bend in the LB cannot be maintained. An elbow in lieu of the LB solves that problem.

Which would be an interesting turn into the house from an outside meterbase without some big ugly sheep hearders hook to contend with.

Oddly enough that same bend of the SEU inside a standard wall depth doesn't really gain you that much as far as the bend radius either.

JAP>
 

HEYDOG

Senior Member
Has anyone ever been failed for installing a 4/0 SEU cable in a 2” pvc from meter to a LB as a stub into the house and converted over with a FA connector.
I have oversized the LB before to make it large enough for the 4/0 SEU!
 

jap

Senior Member
Occupation
Electrician
What is the acceptable bend radius on 4/0 SEU cable?

Did the inspector give any insight as to how to resolve the issue?

JAP>
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Which would be an interesting turn into the house from an outside meterbase without some big ugly sheep hearders hook to contend
There are ways to do it without the Shepard's hook and still use the code compliant elbow.
 

jap

Senior Member
Occupation
Electrician
There are ways to do it without the Shepard's hook and still use the code compliant elbow.

If a 4/0 SEU cable is traveling down an outside 3 1/2"deep wall, are you still not having to make as sharp a bend to turn it 90 degrees out?

A code compliant radius bend of the SEU wouldn't fit inside the wall either if there wasn't there wasn't a brick void or some other gap between the outside wall and the back of the meter base.

JAP>
 

jap

Senior Member
Occupation
Electrician
I just have a hard time believing the inspector failed him for bend radius seeing as how we are discussing a cable installation and not individual conductors that are replaceable when pulled through conduit.

If we had to maintain the bend radius of the conductors, we wouldn't be able to bend them 90 degrees and terminate them in the meterbase.

Which he's going to have to do to make the terminations.

JAP>
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If a 4/0 SEU cable is traveling down an outside 3 1/2"deep wall, are you still not having to make as sharp a bend to turn it 90 degrees out?
You're correct that in some installations an elbow may not be a suitable replacement for an LB due to the length of the sweep.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
SEU has individual conductors that are labeled as one of the types permissible in any Chapter 3 wiring method, if I'm not mistaken? In which case what's wrong with using a cable clamp at the house end of the PVC stub and stripping the SEU jacket inside the PVC? The cable clamp becomes a conversion fitting from cable to PVC.

Cheers, Wayne
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
SEU has individual conductors that are labeled as one of the types permissible in any Chapter 3 wiring method, if I'm not mistaken? In which case what's wrong with using a cable clamp at the house end of the PVC stub and stripping the SEU jacket inside the PVC? The cable clamp becomes a conversion fitting from cable to PVC.

Cheers, Wayne
His inspector seems to be very "Code oriented" and it's likely the individual conductors would not meet 314.28 with a standard PVC 2" LB.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
His inspector seems to be very "Code oriented" and it's likely the individual conductors would not meet 314.28 with a standard PVC 2" LB.
There's 314.28(A)(3), so what's the typical marking on the interior of a 2" LB? If it's 3 @ 4/0, then it's fine. If it's less, then I agree a 2" LB is sized too small for the application.

Table C.11(A) for compact conductors with XHHW insulation says 2" PVC Schedule 40 allows up to (5) 4/0 conductors. So that at least makes it plausible a 2" LB would be marked for (3) 4/0 conductors.

Cheers, Wayne
 

jap

Senior Member
Occupation
Electrician
You're correct that in some installations an elbow may not be a suitable replacement for an LB due to the length of the sweep.

My point was, even without an elbow or LB fitting at all, if the cable itself is inside of a 3 1/2" void between the studs in the wall, your going to have to bend it sharply to be able to terminate it into a meterbase, service disconnect or whatever is on the outside wall you're trying to get into.

Especially if the equipment is mounted directly on the outside wall without that added length of a brick void or the like to allow you to make a sweeping bend to the outside.

JAP>
 

jap

Senior Member
Occupation
Electrician
I read up on this and evidently there is a rule to the bend radius I wasn't aware of for the cable, so, I stand corrected.

That's what I get when I start jabbering without looking things up.

I need to re-read "Charlie's rule" at times. :)

JAP>
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The inspector said the bend radius is wrong. If you use a sill plate the bend radius is even smaller.
I assumed that was his issue and I have to agree with him. Many inspectors will let it slide. My own home has #4/0 SEU in a 2" PVC LB that somehow passed inspection.
 