iwire said:
I believe it is a fact that a properly installed conduit system provides a lower impedance fault path than the EGC normally installed in the raceway.
Bob - I am looking at 'Soares Book on Grounding - 7th Ed.' In Chap. 11 they perform a number of tests and measure fault current on a number of return paths.
Unless I am interpretting their finding incorrectly, they seem to indicate an EGC within the conduit provides the best return path [p. 157, Fault-current study circuit analysis - "The reactance of the circuit include the 'B' conductor (internal EGC) will be the lowest..."].
They go on to say..."Furthermore, unless the conduit was well insulated throughout its entire length [which is usually impossible or impractical in typical commerical installations], there would be a significant number of sparks at stray points to constitute a serious fire hazard."
Earlier comments on the test had indicated: "Some interesting secondary effects were observed in the course of the tests. The fist high-current test produced a shower of sparks from about half of the couplings in the conduit run. From one came a blowtorch stream of sparks which burned out many of the threads. Several small fires set in nearby combustible material would have been serious if not promptly extinguished."
These 'high-current' tests were of a fault magnitude of about 11,000 amps.
Anyway - the way I understand the Soares tests if that an internal EGC provides the best fault clearing path, with the metal conduit being #2....with the potential hazard associated with it.
If I am understanding this incorrectly I would appreciate a clarification. I believe the current Soares edition [8th] makes no changes to this chapter.