For better protection from lightning and high frequency surges, I would like to run a #4 AWG copper grounding electric conductor in the basement of a single family home without using metallic conduit. NEC 2002 Article 250.64 (B) allows this if the conductor is not "exposed to severe physical damage". When referring to #6 AWG copper grounding conductor, the NEC uses "exposed to physical damage". Is there a definition of "exposed to severe physical damage" anywhere?
I know that placing a grounding conductor in a conduit, such as EMT, results in a high impedance for high frequency current. Bonding the conduit and conductor at both ends lowers the impedance, but it is not as good as having no metallic conduit at all.
For better protection from lightning and high frequency surges, I would like to run a #4 AWG copper grounding electric conductor in the basement of a single family home without using metallic conduit. NEC 2002 Article 250.64 (B) allows this if the conductor is not "exposed to severe physical damage". When referring to #6 AWG copper grounding conductor, the NEC uses "exposed to physical damage". Is there a definition of "exposed to severe physical damage" anywhere?