LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor May 7, 2024 #21 I'll settle this. Make the 50a circuit into a feeder and install a small sub-panel. It could even be a two-space if you can find a 2-30/2-20 tandem.
I'll settle this. Make the 50a circuit into a feeder and install a small sub-panel. It could even be a two-space if you can find a 2-30/2-20 tandem.
W wwhitney Senior Member Location Berkeley, CA Occupation Retired May 7, 2024 #22 LarryFine said: Make the 50a circuit into a feeder and install a small sub-panel. Click to expand... If you have two pieces of equipment, one rated for a 50A circuit, and one rated for a 20A circuit, and the load calc is 50A or less, and you have a 50A supply, all you need is a single enclosed 20A OCPD for the 20A piece of equipment. Cheers, Wayne
LarryFine said: Make the 50a circuit into a feeder and install a small sub-panel. Click to expand... If you have two pieces of equipment, one rated for a 50A circuit, and one rated for a 20A circuit, and the load calc is 50A or less, and you have a 50A supply, all you need is a single enclosed 20A OCPD for the 20A piece of equipment. Cheers, Wayne