Shared neutral on LED lighting

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
I hope not as every feeder and service shares a neutral.

The issue that you could have is the drivers are non-linear load so possibly if you maxed out all 3 legs of a multwire branch circuit you might end up with too much harmonic current on the neutral.

Just design the circuits conservatively and you will be fine.
 