jeff43222
- Minneapolis, Minnesota
I had a troubleshooting call in an old house yesterday involving lights and a receptacle all being dead. I went through my usual routine of cracking open the fixtures and looking for a loose connection. At the panel (C-H), everything looked OK until I cracked it open. It turned out that the dead lights and receptacle were on two separate circuits that shared a neutral, but the two breakers were on the same bus. I found two other instances of improper neutral sharing inside the panel. The problem was ultimately solved when I torqued the screw where the shared neutral was connected in the panel. I was a little surprised that this fixed it, as the screw was already pretty tight.
I explained all of this to the homeowner and moved the breakers around so that the circuits sharing neutrals were side by side. I'm curious if other ECs would have done the same. Technically, I don't know for certain which neutrals are being shared by which circuits, as I didn't install the wiring (maybe someone played mix-n-match with the neutrals downstream somewhere). I just went on the assumption that if two hots and a neutral are the sole wires leaving the panel through a given piece of conduit, then they are a multiwire circuit.