I have 7 20A/120V GFI receptacles wired in an 8' long raceway using 2 12g hot wires, 1 12g neutral and 1 12g ground. I have 3 receptacles on 1 hot and 4 on the other. Is there a code either premitting this or against this method. I am being told that in this case you would have to up the gauge on the neutral. Also I have noticed that neutral wires tend to be a little oversized that the hots. Is this to compinsate for such an instence.
 

electricman2

Senior Member
Location
North Carolina
Occupation
Retired Electrical Contractor
Re: shared neutrals

Sounds fine to me. In this case the neutral carries only unbalanced load assuming the hot conductors are not on the same leg.
 

peter

Senior Member
Location
San Diego
Re: shared neutrals

If this is for a computer installation, the specifications may require an oversized neutral to deal with harmonics.
~Peter
 