5-33 Log #1987 NEC-P05 Final Action: Accept in Principle
(200.8 (New) )
_______________________________________________________________
Submitter: Donald A. Ganiere, Ottawa, IL
Comment on Proposal No: 5-49
Recommendation: The proposal should be accepted as submitted.
Substantiation: There are cases where multiple ungrounded conductors having
no potential between them are being installed with a single oversized grounded
conductor. (example: Two #12s on 20 amp breakers both installed on A phase
with a #8 grounded conductor. There is no code rule that prohibits this practice
in the 2008 code. The two specific provisions that use the currently undefined
term of “common neutral, only apply to multi-wire type circuits. If this
proposal is accepted proposal 5-7 must also be accepted.
Panel Meeting Action: Accept in Principle
Revise the ROP draft text to read as follows:
200.4 Neutral Conductors. Neutral conductors shall not be used for more
than one branch circuit, multiwire branch circuit, or for more than one set of
ungrounded feeder conductors unless specifically permitted elsewhere in this
Code.
Panel Statement: The revised text clarifies that the restriction on use of the
neutral in more than one branch circuit is prescriptive and not permissive. The
panel concludes these changes resolve the issues raised by the submitter.
Number Eligible to Vote: 16
Ballot Results: Affirmative: 16