To me this would have been better wording ....
200.4 Neutral Conductors. Neutral conductors shall not be permitted to be used for more than one set of ungrounded conductors unless specifically permitted elsewhere in this Code. [ROP 5-49]
Of course we would need a definition of 'set'.
But, when we are dealing with ungrounded conductors of the same phase or leg, a "Neutral Conductor" doesn't exist.
I hear you but didn't they already change that?
REF post #15 where "mxslick" has 5 conductors A B C A C with one
neutral # 8. How would you simatenously disconnect 5 hots? Wouldn't
the two A phase & two C phase hots be additive on the neutral?
What am I missing ? Thank You John
Not looking to get into the battle this simple question (the OP) caused to start back up - but everything on the transformer or SDS feeding it is one circuit...All MWBC's are single circuits by their very nature, the NEC allows them to be considered "multiple circuits" which they are not.
Roger
Does the OCP divide circuits?
Sharing neutrals can create problems if there are non linear loads. Lighting with electronic ballast,computers,monitors,printers,electronic dimmers and other electronic devices. Harmonics add in the neutral conductor and because there is no protective device(breaker or fuse) to protect the neutral a fire can result. The recommendation is not to share neutrals. And over size the neutral where there are non-linear loads.