here is the scenario:
- Plans call for 3#6 for each 60 A AC unit
- Ac units are located about 150 feet from main panel
- Plans call for the circuits to be run in 3/4" emt
From table 250.122 I see that I must use at least a #10 as equipment grounding conductor.
Questions:
1) Must I use 3/4" emt, or is that a minimum and I can use 1" emt and run both circuits in one conduit, in order to save material and time?
2) If I am allowed to use the 1" or in the case that the plans did not specify the 3/4" emt, do I have to run 2 #10 for the equipment grounding conductor, one for each circuit, or can i just run one #10 and use it for both circuits?
I do not know what the code says about this, but in my opinion it should be fine since there is no current on the equipment grounding conductor, and if one AC fails the equipment grounding conductor will clear the fault, open the breaker, and be ready in case the second one fails, the only picture I can see where it could be troublesome is if they both fail at the same time which is highly unlikely, unless of course lightning but if that happens I don't think separate equipment grounding conductors would make much of a difference in the end result.
I appreciate your help, please include code references. Thanks a lot.
- Plans call for 3#6 for each 60 A AC unit
- Ac units are located about 150 feet from main panel
- Plans call for the circuits to be run in 3/4" emt
From table 250.122 I see that I must use at least a #10 as equipment grounding conductor.
Questions:
1) Must I use 3/4" emt, or is that a minimum and I can use 1" emt and run both circuits in one conduit, in order to save material and time?
2) If I am allowed to use the 1" or in the case that the plans did not specify the 3/4" emt, do I have to run 2 #10 for the equipment grounding conductor, one for each circuit, or can i just run one #10 and use it for both circuits?
I do not know what the code says about this, but in my opinion it should be fine since there is no current on the equipment grounding conductor, and if one AC fails the equipment grounding conductor will clear the fault, open the breaker, and be ready in case the second one fails, the only picture I can see where it could be troublesome is if they both fail at the same time which is highly unlikely, unless of course lightning but if that happens I don't think separate equipment grounding conductors would make much of a difference in the end result.
I appreciate your help, please include code references. Thanks a lot.