But 225 requires a disconnecting means, if you work thru the rules it requires the disconnecting means to be suitable for use as a service disconnecting means, or a panelboard or fused disconnect.

Once you install a panelboard, its no longer a branch circuit, and then a GES is required.

The exemption in 250.32(A) is only allowed in dwelling unit outbuildings or garages, where a snap switch can be used as a disconnect.

Perhaps I'll make a proposal for the 2014 NEC for a FPN to 250.32(A) for the 225 rule.

I have seen non-fused safety switches that are listed as suitable for use as service equipment.

225.36 does not require that the disconnecting means have overcurrent protection, just be suitable for use as service equipment.

Chris
 