They're a bit harmonic-rich, but not enough to overload a conductor that would otherwise have (presuming balanced loading) no normal current.You wouldn't bother upsizing for flourescent lighting and MWBC's???
I do not, but I also design the circuit with only 10 to 12 amps of load on a 20 amp circuit.
Agreed....
Chris,
When you are done with the installation. How about taking some amperage readings and let us know what you ended up with.
I thought it was 10.7A.Can you turn off circuit #20 and see what the neutral reads?
He already did:Can you turn off circuit #20 and see what the neutral reads?
Circuits 22 and 24 only = 10.7A
Why do you only load lighting circuits to 10 or 12 amps. What would be the downside of putting 15 or 16 amps on a 20A circuit.
Overloading on future changeouts (say replacement ballast/lamps
pulled slightly more current).
Less efficient in terms of I?R loss.
The inability to add future luminaires to a circuit, if and when desired.
With common last minute changes to the plans I don't want to worry about if the circuit can handle two more amps. Lighting is usually a continuous load so 16A is the max on a 20A circuit.Why do you only load lighting circuits to 10 or 12 amps. What would be the downside of putting 15 or 16 amps on a 20A circuit.
It would also be interesting to see the neutral load when the circuit is not that expertly balanced. Are you still on that job?
... (presuming balanced loading) no normal current.
And the calculated neutral currents would be 4.7, 6.6, 7.4 and 8.1 respectively. It is interesting for the circuit 14, 16 combination that the calculated current is greater than the measured current. I wonder why.This was the least balanced of the 3 I checked. Again all non-linear.
PNL G1
Cir 12 = 8.6A
Cir 14 = 7.5A
Cir 16 = 4.7A
All on, grounded circuit conductor = 4.2A
Circuits 14 and 16 only = 5.1A
Circuits 12 and 16 only = 8.9A
Circuits 12 and 14 only = 8.3A