Roger,
As Jon has shown the power from the supply system does not change based on the internal motor windings. The power requirement for a 3 phase 10 hp motor is the same for either type of internal connection. It is also the same for either voltage. Look at the current ratings for a dual voltage motor. The current at 240 volts is twice that at 480 volts making the power the same for either voltage. Also look at Table 430.250. If there was a difference in power based on the internal wye or delta connection, then we would need a different table for each type of connection.
Don
As Jon has shown the power from the supply system does not change based on the internal motor windings. The power requirement for a 3 phase 10 hp motor is the same for either type of internal connection. It is also the same for either voltage. Look at the current ratings for a dual voltage motor. The current at 240 volts is twice that at 480 volts making the power the same for either voltage. Also look at Table 430.250. If there was a difference in power based on the internal wye or delta connection, then we would need a different table for each type of connection.
Don