Electron_Sam78
Senior Member
- Location
- Palm Bay, FL
Hey all, give me your thoughts on circuit size and OCPD for this shear I’m wiring for a metal dab shop. The main motor is 30kw which is 40.3 HP. The full load of the whole machine is 180 amps. I’m thinking wire for the full load amps listed in the data plate and OCPD for the largest (main) motor which would be 300a according to chapter 4. FYI, the main motor is not on a VFD in the control cabinet so it does have the full inrush to deal with. The weird thing is the “nominal current” of 120a. I can’t say I’ve ever seen a nominal current and a full load current listed. Not sure what it means in relation to wiring the circuit. This thing is made in Turkey. Thoughts?