Do ship power systems use a neutral? I see a lot of diagrams without them:
They have a hard time finding a 'ground.' :lol:
There is ground, its the ship's haul. :thumbsup:
So only bulk transport ships carrying soil
Seriously, I honestly know next to nothing about ship power, but I recall reading that there are sometimes issues with stray current causing corrosion when connected to grounded shore power.
-Jon
Not an expert but I know a guy that was an engineer in the Navy.
he said it’s an insulated neutral system. If you have a ground fault it turns on a light and the equipment keeps working. Only if you have a second fault will something trip.
he said when someone noticed a light on, they would trip the breakers until the light went off to identify the faulted line. The critical circuits were checked next to last, and the circuits to the captains quarters were very last...
Yes, neutral and ground are two different things although there seems to be a tendency on here to use them interchangeably. I suppose on a ship, the hull would be used as the ground.Not an expert but I know a guy that was an engineer in the Navy.
he said it’s an insulated neutral system. If you have a ground fault it turns on a light and the equipment keeps working. Only if you have a second fault will something trip.
And on the Eisenhower, a sister ship to the nuclear-powered carrier Nimitz, and the nuclear-powered cruiser Arkansas as well. But that part of my work life ended 35+ years ago. So don't rely too heavily on my memory.Charlie B was an electrical engineer on the Nimitz, see if he answers
I have a slight clue. I spent a year (05-06) working in Naval Architecture and Marine Engineering. I did design work on several types of vessels, including tug boats, ferries, and oil tankers. All of them had an ungrounded distribution system. The tankers had a requirement that I had not encountered before. Any circuit that served an outlet of any kind in the vicinity of the oil storage tanks had to originate from a 2-pole breaker. One pole was for the phase conductor, and the other pole was for the neutral.I have no clue about civilian ships
I have a slight clue. I spent a year (05-06) working in Naval Architecture and Marine Engineering. I did design work on several types of vessels, including tug boats, ferries, and oil tankers. All of them had an ungrounded distribution system. The tankers had a requirement that I had not encountered before. Any circuit that served an outlet of any kind in the vicinity of the oil storage tanks had to originate from a 2-pole breaker. One pole was for the phase conductor, and the other pole was for the neutral.
And on the Eisenhower, a sister ship to the nuclear-powered carrier Nimitz, and the nuclear-powered cruiser Arkansas as well. But that part of my work life ended 35+ years ago. So don't rely too heavily on my memory.
The carriers had a 4160 volt delta connection for shore power service, and their generators produced the same voltage. There were step-down transformers to 480 volts for the large motors, but I don't recall whether the secondary windings were WYE or Delta. The cruisers had a 480 volt delta connection for shore power service, and their generators produced the same voltage. Both classes of ships had step down transformers with 120/208V WYE secondary windings. The neutral point of the transformers were not connected to any "ground," and in particular not to the ship's hull.
This was for reliability, as has already been mentioned. If a phase conductor contacted a metal enclosure, for example, it would not result in a short circuit, and no equipment would be out of service. A second phase-to-metal enclosure from a different phase would cause a breaker or fuse to terminate the short circuit. So it was important to discover and fix the first, before the second could happen.
I would like to clarify something said in post #6. The ships on which I served did have a ground detection system. But the ground indicator light did not immediately come on when a phase wire contacted a metal enclosure. Rather, an operator would push a "ground test" button once an hour, during the routine recording of temperatures, pressures, levels, and all other parameters that are monitored throughout the engineering plant. Once a ground fault was noticed, we did turn off circuits one-by-one until the fault was isolated.
Keep in mind that my tour of duty in Naval Architecture and Marine Engineering was 13+ years ago. I believe the power systems were 4-wire, 120/208V, for general power and lighting. They were ungrounded neutral, for the reliability reasons mentioned above. I believe they has the same ground detection system as the navy ships, with a push-to-test-for-ground button. I might have used the phrase "2-pole breaker" incorrectly. I meant to convey that the neutral was switched, and the neutral is disconnected at the same moment the phase conductor is disconnected.So it was a 4 wire system? Why not 3 wire since they got 2 poles already? And how did they get the noodle through the two pole breakers- switching neutral like in gas stations? How were ground faults detected? And why not HRG- ungrounded systems have transient over voltages.
Keep in mind that my tour of duty in Naval Architecture and Marine Engineering was 13+ years ago. I believe the power systems were 4-wire, 120/208V, for general power and lighting. They were ungrounded neutral, for the reliability reasons mentioned above. I believe they has the same ground detection system as the navy ships, with a push-to-test-for-ground button. I might have used the phrase "2-pole breaker" incorrectly. I meant to convey that the neutral was switched, and the neutral is disconnected at the same moment the phase conductor is disconnected.
Switching the noodle is good thing :thumbsup: