And on the Eisenhower, a sister ship to the nuclear-powered carrier Nimitz, and the nuclear-powered cruiser Arkansas as well. But that part of my work life ended 35+ years ago. So don't rely too heavily on my memory.
The carriers had a 4160 volt delta connection for shore power service, and their generators produced the same voltage. There were step-down transformers to 480 volts for the large motors, but I don't recall whether the secondary windings were WYE or Delta. The cruisers had a 480 volt delta connection for shore power service, and their generators produced the same voltage. Both classes of ships had step down transformers with 120/208V WYE secondary windings. The neutral point of the transformers were not connected to any "ground," and in particular not to the ship's hull.
This was for reliability, as has already been mentioned. If a phase conductor contacted a metal enclosure, for example, it would not result in a short circuit, and no equipment would be out of service. A second phase-to-metal enclosure from a different phase would cause a breaker or fuse to terminate the short circuit. So it was important to discover and fix the first, before the second could happen.
I would like to clarify something said in post #6. The ships on which I served did have a ground detection system. But the ground indicator light did not immediately come on when a phase wire contacted a metal enclosure. Rather, an operator would push a "ground test" button once an hour, during the routine recording of temperatures, pressures, levels, and all other parameters that are monitored throughout the engineering plant. Once a ground fault was noticed, we did turn off circuits one-by-one until the fault was isolated.