The UL STANDARD 1950 calls for a 3 wire grounded cord as follows :
3.2.3 Appliance Inlets for Class 1 Equipment shall have an
earthing terminal connected to the protective earthing terminal within the equipment
3.2.4 POWER SUPPLY CORDS SHALL:
Include ,in the the case of Class1 EQUIPMENT, a green/yellow earthing conductor electrically connected to the protective earthing terminal within
the equipment and connected to the earthing contact of the plug, if any;
The information below was taken from The SERVICE MANUAL.
I checked the outlet integrity to make sure that there wasn't a high resistant ground which would not kick the circuit breaker . A high resistant ground can kill you.
Electric Power Source
Use an outlet with a capacity of 115 /120/127V 1,630.Watts or more, or 220-240V, 1712 Wattsor more.
If any other electrical equipment is sourcedfrom thesame power outlet, make sure that the capacity of the outlet is not exceeded.
Use a power source with little voltage fluctuation.
Never connect by means of a multiple socket any other appliances or machines to the outlet being used for the copier.
Make the following checks at frequent intervals:
Is the power plug abnormally hot?
Are there any cracks or scrapes in the cord?
Has the power plug been inserted fully into the outlet?
Does something, including the copier itself, ride on the power cord?
Ensure that the copier does not ride on the power cord or communications cable of other electrical equipment, and that it does not become wedged into or underneath the mechanism.
Grounding
To prevent receiving electrical shocks in the case of electrical leakage, always groundthe copier.
Connect the grounding wire to:
The ground terminal of the outlet.
A grounding contact which complies with the local electrical standards.
Never connect the grounding wire to a gas pipe, the grounding wire for a telephone, or a water pipe.
Separate Ground Wire And UL 1950
The UL STANDARD 1950 calls for a 3 wire grounded cord as follows :
3.2.3 Appliance Inlets for Class 1 Equipment shall have an
earthing terminal connected to the protective earthing terminal within the equipment
3.2.4 POWER SUPPLY CORDS SHALL:
Include ,in the the case of Class1 EQUIPMENT, a green/yellow earthing conductor electrically connected to the protective earthing terminal within
the equipment and connected to the earthing contact of the plug, if any;
The information below was taken from The SERVICE MANUAL.
I checked the outlet integrity to make sure that there wasn't a high resistant ground which would not kick the circuit breaker . A high resistant ground can kill you.
Electric Power Source
Use an outlet with a capacity of 115 /120/127V 1,630.Watts or more, or 220-240V, 1712 Wattsor more.
If any other electrical equipment is sourcedfrom thesame power outlet, make sure that the capacity of the outlet is not exceeded.
Use a power source with little voltage fluctuation.
Never connect by means of a multiple socket any other appliances or machines to the outlet being used for the copier.
Make the following checks at frequent intervals:
Is the power plug abnormally hot?
Are there any cracks or scrapes in the cord?
Has the power plug been inserted fully into the outlet?
Does something, including the copier itself, ride on the power cord?
Ensure that the copier does not ride on the power cord or communications cable of other electrical equipment, and that it does not become wedged into or underneath the mechanism.
Grounding
To prevent receiving electrical shocks in the case of electrical leakage, always groundthe copier.
Connect the grounding wire to:
The ground terminal of the outlet.
A grounding contact which complies with the local electrical standards.
Never connect the grounding wire to a gas pipe, the grounding wire for a telephone, or a water pipe.