goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
I was called to inspect and/or correct a shock hazard problem for outdoor lighting at the lake community facility where I live. There is a 4-circuit outdoor breaker panel mounted on a utility pole adjacent to a volleyball court. Upon my initial inspection I could not find a problem until I replaced the cover to the panel and got whacked. It was hot, I was a bit sweaty but I couldn't duplicate the problem until I leaned back against the metal cyclone fence while trying to replace the cover. Bingo, I got whacked again. I measured the voltage from the outside of the breaker panel to the fence rail and got 120 vac.
This is what I discovered :
Anyone have any other suggestions ?
Thanks.
This is what I discovered :
- The facility is fed by a 120/208V, 3 phase power to the club house
- The initial lighting circuit covering the basketball courts on the opposite side of the play area was 208 volts
- Wiring to that light circuit was run with triplex (seemed OK since no neutral was required at the time that was installed))
- Somewhere along the line (I guess when they created the volleyball area) someone decided to install 120 volt lighting and tapped off the 208 volt power line to the basketball courts. Now we're using the ground wire as a neutral
Anyone have any other suggestions ?
Thanks.