Teaspoon
Senior Member
- Location
- Camden,Tn.
I went on a service call yesterday to find the problem, water Hydrant out side was biteing when touched. This is a rental house, No one living there right now.Owner wanted me to find problem.
On arrival I looked at the ground at meter base & Ground rod looked Ok.
Checked outside Hydrant for voltage, Read 101 volts to ground.
Kitchen sink also had voltage. I proceded to the basement area,
Had voltage on both Hot& cold water lines . By the way this is copper plumbing. I am standing here thinking where to start. Then I notice the water heater. Looks fairly new. I pull the disconnect . & recheck for voltage on water lines all voltage is gone.
Check a little farther to find no ground on water heater, no grounding of water lines. Called owner explained situation and recommended to run a new feed wire to waterheater 10/2 with ground Install new disconnect, and ground the water lines.Owner gave the go ahead to make the Repairs. Really lucky no one was seriously injured from this out of date wiring.
On arrival I looked at the ground at meter base & Ground rod looked Ok.
Checked outside Hydrant for voltage, Read 101 volts to ground.
Kitchen sink also had voltage. I proceded to the basement area,
Had voltage on both Hot& cold water lines . By the way this is copper plumbing. I am standing here thinking where to start. Then I notice the water heater. Looks fairly new. I pull the disconnect . & recheck for voltage on water lines all voltage is gone.
Check a little farther to find no ground on water heater, no grounding of water lines. Called owner explained situation and recommended to run a new feed wire to waterheater 10/2 with ground Install new disconnect, and ground the water lines.Owner gave the go ahead to make the Repairs. Really lucky no one was seriously injured from this out of date wiring.