safetysullivan
New member
- Forth Worth, Texas
Can a normal 4 gain electrical box with knock-out and screw holes be used for a shop made extension cord.
2. The cord set must meet all applicable requirements of Subpart K. For example, the assembly must be marked appropriately (1926.403(g)); boxes intended for use in a permanent installation may not be used (1926.403(b)(1)(i)); cords must be connected to devices and fittings so as to provide strain relief (1926.405(g)(2)(iv)); cords passing through holes in enclosures must be protected by bushings or fittings designed for the purpose (1926.405(g)(2)(v)- fittings designed to fasten cables to metal boxes are not acceptable); and no grounded conductor shall be attached to any terminal or lead so as to reverse designated polarity (1926.404(a)(2)).
Is cheapest way to do it, I've seen many that have unused KO's pushed in or missing after spending some time in use and would rather see an aluminum bell box with threaded entries at the very least, those also not going to meet OSHA requirements though.As Roger mentioned it is not allowed per OSHA, but the shop made extension cords with the proper strain reliefs, double gang 4S box with a double duplex GFCI protected works the best. :happyyes:
And not replace with something acceptable? Sounds like it may get reassembled once he leaves:angel:Not only OSHA, I've had them rejected during a Fire Marshal inspection as well. We had to unplug everything attached to them and disassemble the boxes in front of him before he would sign off on it.
Of course he did not assemble it back together.And not replace with something acceptable? Sounds like it may get reassembled once he leaves:angel:
You can repair a cord with listed parts, you can not use a 4"sq box.On another note, you can't throw away good extension cords every time the ends get messed up.
Roger
There is lots of things I don't know and "listed parts for extension cord repair" is one of them. Do you have a link?
Are you under the impression a cord cap can not legally be replaced on an extension cord?Listed for repairing cords is one thing.
OSHA allowing repaired cords on a jobsite is another.