SHORE POWER AND RESI LOAD CALC

Status
Not open for further replies.

florida-sparkey

Senior Member
Location
Pinellas Park, Florida
Occupation
Master Electrician
Hello all and thanks for lookin at my post!

I am doing a residential load calc.

They have 2 shore power connections rated at 30A / 240V. (They do have 2 boats with unknown loads.)

I am inclined to use both at full value in my calc.

This pushes the calc way up over 200.

Am I making a mistake?

Thanks!
 
Look at 555.12.

The article does not say resi, but in the 2017 it has been changed and does.

THANKS!

Looks like 2 receps with one each in 2 slips would be 100% per the change you stated in 2017. (2011 and 2014 NEC marina and boatyards to include residential. We are still on 2011 here)

Someone just got a service upgrade!
 