weressl
Esteemed Member
Different situation entirely, there is no transformer here.
Sure there is, the DC transformer........:smile:
Different situation entirely, there is no transformer here.
Originally Posted by iwire
Different situation entirely, there is no transformer here.
Given that this is probably a 100% generating facility, all solar panels will add to the SCA less their respecitve cable impedance. This must be calculated using either IEEE or IEC standards. The utility company probably wants to know how to protect their system given a fault at the generating solar site. As I stated earlier, these computations must be performed by an engineer educated in short circuit studies or using a competent software program of which there are only a few capable of accurately performing SCA values. Site testing is not an option, using the rated SCA of any device is also not an option, and using one's opinion is also not an option.
Sorry to be so frank but the resulting SCA values are very important to not only protect the generator's site but also the utility lines and the workers if exposed to the short via arc flash and arc blast.
To iwire...
Have you worked with utility interactive PV systems? - Yes
The total Isc of my 50 KW system is under 200 amps - Good for you. However, does HIS system exactly match yours?
I will be frank as well, it is not complicated and it does not take an EE to figure it out.
That's some statement...I'm afraid to ask how you computed your SCA values.
I'm afraid to ask how you computed your SCA values.
Well Pilgrim, brain surgery is just the same as taking a bullet out....... You heat up a knife, a bigune, waste some good bourbon where it gone in and just dug in.....we don't need no stinkin' brain surgeons.....![]()
We are not talking about brain surgery, we are talking about putting a band aid on a boo boo.
Sorry to let you in on this but EEs are not needed for every electrical project.![]()