Sometimes I will run into and installation that I am unsure of if it is suitable. Then I will request the letter from an engineer...passing the responsibility of my approval directly on to the engineer.
And that is very appropriate. We each have our responsibilites, the engineer to design, the EC and Inspector to install. When the engineer/EC/Inspector have concerns, it is appropriate to discuss, ask questions, get answers, and keep for the record, with the responsible party making final judgement, and sometimes that is the Engineer, sometimes its the Inspector.
Markstg,
Just as a note, I've done countless short circuit, overcurrent PD coordination and arc flash studies and have not been asked to sign/stamp/seal any of them. Although it would be easy enough to do so, but I've never been asked.
Normally I would not think that you submit these calculations (as you don't submit the numerous calculations for cable sizing etc.) as part of the "Issued for Contruction" documents. But if you did, just as you Seal the drawings, I would think you would seal your submitted short circuit studies, if you submit them outside your office, say to the owner for record. In my state all documents produced for Contruction or submitted to the owner for record that are produced by the Engineer must be sealed.
I would not approve it, as I mentioned, I would pass it on.
I was just curious as to who is actually looking at the studies? Is there ever a challenge to the study as being improperly performed?
The electrical engineer of record, ie. the one who has responisble design, is looking at, and probably produced the study.
Generally no one challenges the studies, as in almost all cases, the study is done correctly. But when a circuit breaker trips when everyone thinks it shouldn't have, (eg, the main trips when the fault was sownstream on a sub feeder or branch circuit)the engineer may be called upon to review, and he most likely will look at the study prior to making any changes. Worst case, a circuit breaker doesn't trip, say because its instaneous is set to high, causes damage to equipment. Someone is going to be asking some questions.
I have a question.....On circuit breakers that have a high/medium/low instantaneous trip adjustment, who selects what position to put it in. In my experience, its left where the manufacturer set, unless it trips, then it is set to high. Should the EC set it, should the Engineer tell the EC where to set it? Does it matter?