So I received a Bldg Dept comment requesting short circuit calculations for a roadway lighting project. This is the first time I've been asked for this in over 20 years of roadway lighting designing. The power company provided the following information:
Max Available Fault Current at the transformer secondary terminals is 53205 symmetrical amperes at 120/240 volts.
The protective device on the line side of the transformer is a 25-amp type KS fuse.
The primary service voltage is 13.2kV L-L.
The lighting panel board will be 100 amp, 120/240V single phase
What is the correct method of calculating the short circuit amps for the given condition?
Thanks in advance for your help.
Max Available Fault Current at the transformer secondary terminals is 53205 symmetrical amperes at 120/240 volts.
The protective device on the line side of the transformer is a 25-amp type KS fuse.
The primary service voltage is 13.2kV L-L.
The lighting panel board will be 100 amp, 120/240V single phase
What is the correct method of calculating the short circuit amps for the given condition?
Thanks in advance for your help.