Markdegracia0370
- Davao
Is the 4160 system utility or customer owned? You can start with just figuring out what you get at the secondary of the transformer assuming infinte primary fault current. This would be full load current divided by the impedance, or in your case about 31.4K. Then you can use this calculator to find the available fault current at the end of your conductors:
https://www.mikeholt.com/freestuff-shortcircuitcalculations.php
Generally I would go with those values, but if it really would save you a bunch of money and hassle if the fault current was lower, you could take into account the impedance of the primary, but it can be hard to get values for this from the utility. Dont forget about your series ratings if applicable.
Hi guys;
Can you help with this, in how to calculate the short circuit calculation of this single line diagram to properly size the protections.
Please see attached file
Hi guys;
Something is odd about this SLD. You have cable going between the LV SWGR main and the LV SWGR bus. This would be directly connected together unless mounted separately; but why, when most manufacturers provide it internal. Also, why so many 400A breakers? A typical LV SWGR lineup has 4 breakers per vertical section, and the cable would directly go out to the motor control, and not need an intermediate 400A breaker.
Do you also need to set protection on the VCB ahead of the transformer?
Curious as to what is this facility?
Regardless, you need the SC info at the HV side of transformer to proceed.
This is the substation set-up we design at underground (70meters below the ground). From VCB to the Distribution Panel (8 units of 400A CB) was installed at Underground and the recloser/Cutout was installed at the surface.
Its very hard to calculate the SC due to continuous advancement of the underground operation and of course our cable will also consistently extending.