Short-circuit impedance tolerance of Power Transformers

Merry Christmas

Joao

Member
Location
portugal
Occupation
engineer
My question:

As per IEC 60076-1 is allowed uk% tolerances (positives and negatives).

For short circuit issues is possible to request to manufacturers that NEGATIVE TOLERANCES are not allowed? Or even BOTH TOLERANCES?
 
My question:

As per IEC 60076-1 is allowed uk% tolerances (positives and negatives).

For short circuit issues is possible to request to manufacturers that NEGATIVE TOLERANCES are not allowed? Or even BOTH TOLERANCES?
Probably not without spending an inordinate amount of money

Tolerances exist partly because %Z is theoretical until after the transformer is manufactured and actual measurements can be performed.
 
You can specify a minimum impedance without too much additional cost, but there will still have to be an acceptable tolerance above the specified minimum.
Yes, we have raised this issue with one Vendor and feedback was that tolerance could be decreased like for example +-5% instead +- 7,5%
 
Reducing the tolerance range will certainly increase your transformer cost. Why do you feel you need to do this?
Because we are facing issues with Short circuit current levels in 33 kV Switchgears. We want to keep below 31,5 kA. In this project unfortunelly we have start the project from the ROOF.
 
Question: if the manufacturer typically supplies transformers that have a +-5% tolerance, would it really cost much more to get a -0% +10% tolerance.

It seems that the OP's situation could handle a typical range of possible impedance values, but with a hard minimum to that range.
 
I think it's easier for the manufacturer to hold to a specific impedance with their standard tolerance than a tighter tolerance on standard impedance. Just calculate the impedance you need and add the standard tolerance, then give that to the manufacturer as the minimum.

So 31.5 kA @ 33 kV = 1,800 MVA. For a 100 MVA transformer, you would need 100/1800 = 5.6% minimum impedance. If the tolerance is ±7.5%, then for the low end of the tolerance to be 5.6%, the nominal impedance needs to be 6%.
 
Question: if the manufacturer typically supplies transformers that have a +-5% tolerance, would it really cost much more to get a -0% +10% tolerance.

It seems that the OP's situation could handle a typical range of possible impedance values, but with a hard minimum to that range.

I do not know. What I can inform you is Vendor told me that they could decrease the tolerance, but never DEVIATE that tolerance.
 
I think it's easier for the manufacturer to hold to a specific impedance with their standard tolerance than a tighter tolerance on standard impedance. Just calculate the impedance you need and add the standard tolerance, then give that to the manufacturer as the minimum.

So 31.5 kA @ 33 kV = 1,800 MVA. For a 100 MVA transformer, you would need 100/1800 = 5.6% minimum impedance. If the tolerance is ±7.5%, then for the low end of the tolerance to be 5.6%, the nominal impedance needs to be 6%.
Yes in general if you request some like: NEGATIVE TOLERANCE IS NOT ALLOWED, they will DEVIATE IT.
 