Turn the Main and every breaker off in the panel. even the Gen feed.
Start the Generator. Does its CB remain on? Is it a GFCI? Yes, you passed step 1. No, well not so good. Start over.
Next check voltage on the back feed generator circuit breaker. What are your voltages? 240 L1-L2, 120 L1-N, 120 L2-N.
No, back up you have something wrong.
Clamp a couple amp meters on each incoming generator lines. Set them to catch MAX current while still monitoring voltages.
Turn on the Gen fed CB. Nothing should have changed.
Turn on one single pole circuit. Note current and voltage. Check running amps.
Repeat...
Do not exceed the generator capacity.
Nothing more than any one else has said. One step at a time.