Trying to install a 3/4" RMC conduit from an existing stub up to an existing jbox which requires the installation of an elbow. This is located in a C1D1 Group D location (inside a gasoline dispenser). Existing 3/4" RMC conduit is stubbed up. Per 501.15(A)(4), the first fitting to be installed to the existing stub-up will be a seal-off (25%fill). Installing (1) cable with .42in OD once the conduit run is complete. Due to an overhead obstruction, a 3/4" RMC elbow compliant with Chapter 9 Table 2 radius is not possible. Additionally, there is not enough vertical clearance to install a close nipple followed by a C1D1 pulling elbow (the elbow will fit, there is not enough room to install/remove the cap due to being threaded). It appears the only viable option is using a short radius elbow such as an Appleton ELMF90-75. However, emailing the manufacturer of the short radius elbow, they state "short radius elbows are only for use right at the box or enclosure and cannot be used in the middle of a conduit run (jbox is approx. 12-14" away from stub up location)."
A short radius elbow (no removable cover) - seems very hard to pull through in the middle of a run. However, I am looking for a code section to verify the manufacturers comments that short radius elbows are only for use at the box or enclosure.