New install. Parallel runs on the 120/208Y secondaries were ohmed out and connected at the secondary bushings of the 300kVA 3 phase deadfront padmount transformer. Customer was responsible for landing secondaries at his switchgear. Transformer was energized with pole mounted overhead fuse disconnects. Two fuses blew and the substation breaker operated with 2500 amps overcurrent trip on two phases. The high side is 14.4/24.9Y. Substation is 1/2 mile from this customer. Two conductors on the secondary at switchgear were crossed and there was a short circuit on two secondary phases.
I contend that the secondary fault could never create the high side amps recorded and asked for a TTR test. TTR came back within limits.
Does anyone believe the estimated 15K infinite buss fault current could have caused the 2500 amp fault on the high side? Estimated transformer impedance 5%. No customer load on the transformer when energized.
Was the TTR the best call? What other test should should be requested?
Substation operations affected a major customer and we are not prepared to energize transformer again while that customer is online.
Any other things to consider?
Thanks,
Thanks,