I am currently involved with the installation of a 10-generator paralleled system where each generator is 480V wye at 375 KW. There are no neutral conductors going from the generators or coming from the utility transformer. There are no neutral conductors in any of the six transfer switches. I am told the utility is a delta transformer. My question is, do we need to ground the neutrals at each of the 10 generators to provide a ground fault path back to the source (2005 NEC 250.2)? The owner of this particular facility says that we are not to ground the neutral of the generators. What do you think?
To not ground the generators, IMO, is not an option. Since these are relatively small generators, solidly grounding the system might be reasonable. Are there any 277 Volt loads? Evidently not, if the utility didn't have a neutral either. If there were 277 Volt loads, then there is no option. The generator must be grounded.
The generators could be grounded through high resistance systems, but this can be pretty expensive by the time you figure in all the monitoring hardware.
A literal (what other kind is there???) reading of 250.20 (B) would seem to indicate that you do not need to ground the neutral point of the generators.
(1) doesn't apply because the voltages are not limited to below 150
(2) doesn't apply because, although this is a WYE, there is no neutral conductor that is being used as a circuit conductor
(3) doesn't apply because it is not a high-leg system
250.20 may not require it, but it sure seems like 250.4 would require it.
If they hold to their position of not connecting a system bonding jumper (Your original post said 'ground' but then you stated that it was for providing a fault path) then i'd start asking lots of questions.
"If i don't install a system bonding jumper, then how will the system clear in the case of a ground fault"? and on and on until all the questions are answered.
Good luck. Let us know what happens.