GEC, Grounding Electrode Conductor.Is there ever an exception that there may be voltage and amps on the main egc leaving meter base to the ground rod? If so, what are numbers not to be too concerned about or should it always be 0 in a perfect world ??
Amps 0.2 - 4.9
Volts 5 - 57V
Yes details, exactly what two points and under what conditions are you measuring those voltages?
I took most measurements around the #6 bare copper from ground rod as it entered into meter base for amps
I took the voltage readings 10" from earth, scraped paint off GEC and stuck other prob in earth about 8" wet soil
Upon arrival house on in normal mode
Amps 1.7 amps
Volts 57
After Shutting down both main breakers in house (another storyline)
0.7 amps
57 volts
Other odd readings
When taking apart a 240V well circuit (when off or on) sparks from egc and all kinds of voltages from 30-157V on egc to egc same circuit
Illegal sub panel on a 3 wire off 1 panel with grounds and neutrals together on floating bar (not bonded) 103V from neutral bar to anything metal
As we isolated circuits seems like septic and well circuits caused the most fluctuations
Another note Main neutral that fed Main panel was loose. After giving it about 4 full turns Amps on GEC went from 1.1 to 4.9
Multiple bootleg (cheater) neutral to ground connections.
Long story short seems like the more I corrected and tightened things the worse the readings and bigger the sparks on the egc wires
Sounds to me like you have a bad neutral somewhere, even though you possibly fixed some potential bad spots, there is still something upstream from where that GEC is connected to neutral, which is apparently in meter base. Cheater neutral to ground connections are a problem, but not a direct contributing factor to this particular issue, you have an open circuit or high resistance in the neutral somewhere between your GEC connecting point and the source (POCO transformer).
That is because with the bad service neutral everything bonded to it (including all equipment grounding conductors) is seeing this same rise in voltage above true ground. A GFCI will do nothing to protect from a rise in voltage on the EGC.I forgot another interesting tidbit. When HO was getting (lifting) his kids out of hot tub other night (in sandals on cement base pavers) he said he definitely was getting shocked (mild but was for sure shocked) until they were all the way out. I inspected hot tub and was wired correctly (4 wire and on gfci)
Good chance there has been some 120 volt equipment failures in that place as a result as well.Get the POCO involved and look for a poor or missing neutral connection. Now. not later No more hot tubs, no baths, showers or excuses.
Get the POCO involved and look for a poor or missing neutral connection. Now. not later No more hot tubs, no baths, showers or excuses.