Looked it up again, an MGE PMN084 42 225. Here's the installation manual pdf:
http://www.apcmedia.com/salestools/MBPN-7SPHE4_R0_EN.pdf
and look at page 39 of 58, 3.4.3.1 grounding. It's really worded badly where it calls for the safety ground to originate at the utility service equipment and says "OR" other acceptable building ground, such as the building frame ...
Drawing is on the same page with the same omission, showing the EGC coming in with the feeder with an earth ground symbol. The unit obviously needs both an EGC and a GEC. The drawing needs a GEC on it.
This unit is mated to an adjacent cabinet that is a dual source static switch and the feeders are not sourced at the "service", they originate at DP switchboards, which have an EGC but no GEC available. The "service" point is ~ 80 ft away in a much larger 2N switchboard. There are two redundant 2(N+1) UPS rooms that source the feeders. This is the typical installation.
Interesting artifact. In my mail way prior, I stated that connecting the two different EGC busbars, from two different UPS rooms, together at the static switch would cause a small equalizing current to flow over the EGCs as they came together at the static switch, however connecting an Ibeam to any other I beam in the building with wire similar would cause no current to flow. The EGCs would be noisy and the Ibeams would be quiet. The GEC was necessary because 250-30(A)3 required it and because it serves a different purpose, a clean quiet reference point (low impedance path) to the equipotential earth ground.
The EGCs in place have 4 amps of noise on them in service.
Have at this, does this drawing and paragraph 3.4.3.1 meet code or not.