Show window on timeclock?

Status
Not open for further replies.
chevyx92 said:
You have to either compute the loads as follows:
1) unit load per outlet OR
2) 200VA per linear ft

So if you have a 16 linear ft of window, then (16 X 200= 3200 VA)
3200VA/120V = 26.66A. That means you need at least (2) 20 amp circuits.

If you knew the load that would be plugged into the outlet then you could use that and determine if a single circuit would suffice. Otherwise you need to use 180VA per outlet.

Thanks for feedback, I will be challenging this timeclock issue next inspection. We'll see.:cool:
 
nyerinfl said:
I will be challenging this timeclock issue next inspection.
In case your inspector does site the FBC, have him read this again.

FBC 13-415.1.ABC.1.1 Automatic lighting shutoff.

Interior lighting in buildings larger than 5000 square feet (465m?) shall be controlled with an automatic control device to shut off building lighting in all spaces.
 
You may want to look into the "Energy Codes" for your state - if anything like mine - they may still have some exemptions or still other requirements for things like show windows, display lighting, signage, etc. That may require a time clock or photo-cell.... And even still - a time clock of a particular type.
 