chevyx92 said:You have to either compute the loads as follows:
1) unit load per outlet OR
2) 200VA per linear ft
So if you have a 16 linear ft of window, then (16 X 200= 3200 VA)
3200VA/120V = 26.66A. That means you need at least (2) 20 amp circuits.
If you knew the load that would be plugged into the outlet then you could use that and determine if a single circuit would suffice. Otherwise you need to use 180VA per outlet.
Thanks for feedback, I will be challenging this timeclock issue next inspection. We'll see.