shower and tub space

Status
Not open for further replies.

kendog

Inactive, Email Never Verified
I think they should add something that states exactly what the shower and tub area is for recep and switch. some of the edition say you cant install a switch or recep in a shower or tub area unless it part of the shower or tub assembly and others say you can't intsall a recep in a shower stall and a switch can't be installed in a shower space. A what shower space the only thing that comes even close to giving you a describtion of a shower space is for luminaries. Please give me some feed back.
 

charlie

Senior Member
Location
Indianapolis
Re: shower and tub space

It sounds like you want to make a definition as to what constitutes a shower or tub space. Put it into writing and let us chew on it. :D
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: shower and tub space

NEC-2005 406.8(C) Bathub and Shower Space. Recptacles shall not be installed within or directly over a bathtub or shower stall.
NEC-2005 404.4 Wet Locations. A switch or circuit breaker in a wet location or outside of a building shall be enclosed in a weatherproof enclosure or cabinet that shall comply with 312.2(A). Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.
Have you experienced confusion regarding these codes? They seem self-explanatory without definition.

Look at the welcome message at the top of this area, and rephrase your proposal. It might be clearer that way.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: shower and tub space

(C) Bathtub and Shower Space. A receptacle shall not be installed within a bathtub or shower space.
This has been cleared up a bit in the 05 code. Look at the wording I have posted from the 2002 code and compare that to what George posted from the 2005 code.
Don
 