A 3 phase 208 200 amp shunt trip breaker being used as a main service disconnect, best location to get the 120 volts to engage shunt?
Welcome to the forum.A 3 phase 208 200 amp shunt trip breaker being used as a main service disconnect, best location to get the 120 volts to engage shunt?
It's merely way of tripping it remotely. Once the tripping power is removed, it can be reset manually.This may be a stupid question, but why would someone shunt trip a main? Wouldn’t that negate turning the breaker back on?
No, a shunt-trip breaker does not need power to stay on. It's basically a standard breaker with a solenoid coil added that activates the trip mechanism. A momentary pulse of power trips it.Doesn't a shunt trip have to have power to remain closed? If so, wouldn’t the control circuit be after the main?
Thanks.It's merely way of tripping it remotely. Once the tripping power is removed, it can be reset manually.
No, a shunt-trip breaker does not need power to stay on. It's basically a standard breaker with a solenoid coil added that activates the trip mechanism. A momentary pulse of power trips it.
What NEC code section would require this?Thanks all for your comments, shunt is because there is 20 town homes (SFD) that require a disconnect on each dwelling and the engineer designed a meter stack system, so each unit gets a service disconnect shunt button on each unit.
Probably a local code, don’t know why they would want individual owners to be able to kill power to the entire complex. I can see maybe a fireman’s switch. Done that on commercial buildings as a local requirement because the main is inside.What NEC code section would require this?
Here's a Google Maps link to a pic of one. I know because I have worked there.Three phase to a dewelling.first for me
Is this shunt trip service disconnect remote from each of the 20 units? If so then how's does it comply with 230.71(A)(1)?NEC 230.70(A)(1), A(3) allows remote control, 230.85 signage.
So the service disconnects are not on each separate structure? If that's the case then each unit is fed by a feeder not SEC's.Art 230.70(A)(1) states or inside nearest the pointor the service conductors, the meter Paks are 2 inches off the complex structure in the alley way. All good to go. See you all with any future questions. Thanks and best.