A 3 phase 208 200 amp shunt trip breaker being used as a main service disconnect, best location to get the 120 volts to engage shunt?
 
A 3 phase 208 200 amp shunt trip breaker being used as a main service disconnect, best location to get the 120 volts to engage shunt?
Welcome to the forum.

Generally, any always-hot source supplied by the breaker will do, unless it's rated to be continuously energized.
 
Just use a 15 amp branch circuit from the panel. What is the purpose of the shunt trip?
 
This may be a stupid question, but why would someone shunt trip a main? Wouldn’t that negate turning the breaker back on?
Doesn't a shunt trip have to have power to remain closed? If so, wouldn’t the control circuit be after the main?
 
This may be a stupid question, but why would someone shunt trip a main? Wouldn’t that negate turning the breaker back on?
It's merely way of tripping it remotely. Once the tripping power is removed, it can be reset manually.

Doesn't a shunt trip have to have power to remain closed? If so, wouldn’t the control circuit be after the main?
No, a shunt-trip breaker does not need power to stay on. It's basically a standard breaker with a solenoid coil added that activates the trip mechanism. A momentary pulse of power trips it.
 
It's merely way of tripping it remotely. Once the tripping power is removed, it can be reset manually.


No, a shunt-trip breaker does not need power to stay on. It's basically a standard breaker with a solenoid coil added that activates the trip mechanism. A momentary pulse of power trips it.
Thanks.
Makes sense now.. Don’t ever remember coming across one like that before.
I had in mind something like a contractor with an aux relay.
 
Thanks all for your comments, shunt is because there is 20 town homes (SFD) that require a disconnect on each dwelling and the engineer designed a meter stack system, so each unit gets a service disconnect shunt button on each unit.
 
Thanks all for your comments, shunt is because there is 20 town homes (SFD) that require a disconnect on each dwelling and the engineer designed a meter stack system, so each unit gets a service disconnect shunt button on each unit.
What NEC code section would require this?
 
What NEC code section would require this?
Probably a local code, don’t know why they would want individual owners to be able to kill power to the entire complex. I can see maybe a fireman’s switch. Done that on commercial buildings as a local requirement because the main is inside.
 
Shunt only does each single family dwelling, Not entire complex, each dwelling is fed with a 200 amp 3 phase 208Volt breaker.
 
If that’s the case, then probably pull from a house panel, if there is one. Where is the shunt button located? At each unit? If so, then it could be powered from the tenants panel since you have to run two wires back to the breaker anyway.
 
I could see this if there was no main in the residents panel. I remote would do the trick. Never seen one in a meter pack. A pic would be cool to see.
 
I would pull it from the panel in dwelling unit, pull with feeder to unit. I take it is all in raceway or MC.
Wonder if a branch circuit can be in the meter pack with feeders/ service conductors. Ummmm
 
I worked on one in the Dominican Republic that had a 400 amp three phase service. 24’ ceiling in the living room, three phase washing machine. Commercial dryers. It was the guy’s vacation home. He said his regular home in Puerto Rico was even bigger!
 
Art 230.70(A)(1) states or inside nearest the pointor the service conductors, the meter Paks are 2 inches off the complex structure in the alley way. All good to go. See you all with any future questions. Thanks and best.
 
Art 230.70(A)(1) states or inside nearest the pointor the service conductors, the meter Paks are 2 inches off the complex structure in the alley way. All good to go. See you all with any future questions. Thanks and best.
So the service disconnects are not on each separate structure? If that's the case then each unit is fed by a feeder not SEC's.
 