on the ups system do you have to have a shunt breaker on the primary side,and the load side.this is in case of a fire,so the fireman can kill all power.
on the ups system do you have to have a shunt breaker on the primary side,and the load side.this is in case of a fire,so the fireman can kill all power.
on the ups system do you have to have a shunt breaker on the primary side,and the load side.this is in case of a fire,so the fireman can kill all power.
Most if not all hardwired UPS will have built in terminals for shut down from an external EPO.
that EPO should kill primary and battery. write
Killing the supply to a UPS will not stop it's output, that is why you would use the on board terminals to get it done.
I just like to know,if there was a fire in the room shouldn't the EPO SWITCH kill all power in the room.
I just like to know,if there was a fire in the room shouldn't the EPO SWITCH kill all power in the room.
on the ups system do you have to have a shunt breaker on the primary side,and the load side.this is in case of a fire,so the fireman can kill all power.
It is not that easy.
First the NEC does not really require an EPO at all. You can have a room full of computers, servers UPS systems and not have an EPO.
However if you have an EPO and satisfy all the other items listed in 645.10 then the NEC allows you to do more of the power wiring in the room with flexible cord.
If you chose to go the EPO route then the EPO must shut down the power to the electronic equipment. The lighting power can stay on.
I can't stress enough that if you really need to know about this pick up the NEC and read Article 645, it is not long but it could save you a lot of grief.
Killing the supply to a UPS will not stop it's output, that is why you would use the on board terminals to get it done.