shunt trip breaker/E-stop circuit
It's actually been found out to be a latching contactor, these type don't look like a regular contactor, because they are low profile to fit inside a panelboard enclosure. they have built in clearing contacts, so constant voltage is Ok. Something like this: http://www.emersonnetworkpower.com/en-US/Products/PowerSwitchingandControls/IndustrialControls/LightingControls/Pages/ASCO920LightingContactorsforFeederCircuits.aspx
The multiple wires are used to either incorporate the integral switch that opens when the breaker is tripped, or to bypass-it. If you bypass it, make sure that the trip signal is momentary so that you don't burn up the coil by keeping power on it.
Hope this link works: http://www.google.com/imgres?q=shun...&ndsp=35&ved=1t:429,r:11,s:0&biw=1280&bih=853
Sorry but it doesn't.
The Carling device you refer is about 'shunting' around the overload sensing portion of the breaker. It is not about a 'shunt trip' coil as they are normally applied in molded case breakers.
The Carlin unit is wired the SAME way how a shunt trip is assembled. At that moment I could not find an appropriate link to the shunt trip, but if you doubt it I will find it for you.:happyyes: