Shunt trip breakers for equip. under kitchen hood
faresos
Hello every one:
I have a question regarding shunt trip breakers for equipments under commercial kitchen hood; We have many shunt trip breakers in one panel and I'm not sure what does activate these shunt trips breaker, is it a signal from Ansul system control panel or the signal should come from the fire Alarm control panel?
Thanks,
Sam
Hello every one:
Thanks,
Sam
It should be from the Ansul system micro switch however, it may need to go through a relay first depending on the number of functions that are being controlled from the switch.
Roger
Simply, it's a tripping voltage from a NO terminal on a microswitch that had power on its common terminal.
Make sure the shunt-trips can withstand constant energization if the tripping voltage remains after the trip occurs.
They can, you just had some bad luck.
I have, but some ST breakers come with warnings that the coil should not be continuously energized.
To assure this doesn't happen, have the voltage supplied by a ST breaker itself, or use aux. contacts.