The client wants a shunt trip on all 20A molded case circuit breakers for panelboard. This seems very unusual to me - not sure what the typical application would be for this?
Its so the PLC can shut the load down and force a manual reset.Thanks.
This is an industrial plant—waste water treatment.
Could be - but for futureIts so the PLC can shut the load down and force a manual reset.
Great question. I’ll check into next weekAnd what are they using to control these shunt trips? A separate control for every circuit breaker?
Then the wifi and hvac would go offWhy not get a main shunted CB
Good point. Would have to have a designated panel with all emergency off circuits separated.Then the wifi and hvac would go off
Usually with the gas pumps and canopies, they have an auxiliary contact on the breaker to disconnect the neutral too.I forgot about gas pumps. I knew I had seen some on 20 but couldn't recall where.
I don't believe a E-stop operation would be required to open the grounded conductor. You could still have a "fuel panel" with shunt trip main or feeder breaker and still have switched neutral breakers on branch circuits where needed. I think many fuel control systems have input leads for an E-stop button and it just locks out the controls if stop is pushed and never shuts off any branch circuit breakers.Usually with the gas pumps and canopies, they have an auxiliary contact on the breaker to disconnect the neutral too.