Sorry if this repeats an earlier post. I tried to find an answer in the forum, but a search on "shunt trip" produces hundreds of hits - this forum is HUUUGE!
Is shunt trip breaker design standardized?
In doing a design I have to balance my panel loads, or at least total them up. Shunt trip breakers have been a bit of a dilemma. At least for lower amperage breakers, the shunt trip breaker uses an extra slot, or pole (I've taken to calling it the "shunt pole"), in the panel, but doesn't electrically connect to that pole. I need to know which side of the breaker the shunt pole is on. That is, if a shunt trip single pole 20A breaker is installed in the very top left of the panel, is the load on the A phase (slot 1) or on the B phase (slot 2)?
I asked my Eaton rep this question and this is what I was told regarding Cutler Hammer's shunt trip breakers:
(Large case breakers, 3P100 and above, do not require an extra space). For the smaller breakers, the shunt pole is on the bottom when the breaker is installed on the left side of the panel.
But my problem is that I've only actually seen Square D breakers, and they're exactly the opposite. In fact, I found a picture of one elsewhere in this forum, and it illustrates it perfectly.
So, did my Eaton Rep not understand the question, or does the design vary from manufacturer to manufacturer?
Thanks
Is shunt trip breaker design standardized?
In doing a design I have to balance my panel loads, or at least total them up. Shunt trip breakers have been a bit of a dilemma. At least for lower amperage breakers, the shunt trip breaker uses an extra slot, or pole (I've taken to calling it the "shunt pole"), in the panel, but doesn't electrically connect to that pole. I need to know which side of the breaker the shunt pole is on. That is, if a shunt trip single pole 20A breaker is installed in the very top left of the panel, is the load on the A phase (slot 1) or on the B phase (slot 2)?
I asked my Eaton rep this question and this is what I was told regarding Cutler Hammer's shunt trip breakers:
(Large case breakers, 3P100 and above, do not require an extra space). For the smaller breakers, the shunt pole is on the bottom when the breaker is installed on the left side of the panel.
But my problem is that I've only actually seen Square D breakers, and they're exactly the opposite. In fact, I found a picture of one elsewhere in this forum, and it illustrates it perfectly.
So, did my Eaton Rep not understand the question, or does the design vary from manufacturer to manufacturer?
Thanks