An electrician called me today informing me that he has a GE THQB1120STI 120v shunt breaker to wire to a fire panel that is controlling 480v equiptment. I am under the impression that he needs either a 480V shunt breaker or a kit for the breaker. I have only received 2 drawing from the rep with this comment but i can't find a way to paste them on this thread.
WHEN A SHUNT TRIP IS ADDED TO A Q-LINE BREAKER, IT'S SIZE IS INCREASED BY ONE POLE, CAUSING A 1-POLE BREAKER TO LOOK LIKE A 2-POLE, A 2-POLE LIKE A 3-POLE, ETC. THEREFORE, THE CUSTOMER WILL NEED SPACE IN THE PANELBOARD FOR ANOTHER POLE IN ORDER TO ACCOMODATE THE ADDITION OF THIS ACCESSORY.
thanks
for any advise in advance
WHEN A SHUNT TRIP IS ADDED TO A Q-LINE BREAKER, IT'S SIZE IS INCREASED BY ONE POLE, CAUSING A 1-POLE BREAKER TO LOOK LIKE A 2-POLE, A 2-POLE LIKE A 3-POLE, ETC. THEREFORE, THE CUSTOMER WILL NEED SPACE IN THE PANELBOARD FOR ANOTHER POLE IN ORDER TO ACCOMODATE THE ADDITION OF THIS ACCESSORY.
thanks
for any advise in advance