Shut trip for elevator

AC\DC

Senior Member
Location
Florence,Oregon,Lane
Occupation
EC
Attached is a diagram—— the fire alarm told me shut trip and fire alarm are reversed—- I have not made it out to see what the guys landed. But 5-9 should be the 120 volt shut trip - and the power monitoring should be 1 and7 since it’s just a contact that drops off once shut trips to then trigger alarm
 

Attachments

  • IMG_5894.png
    IMG_5894.png
    652.3 KB · Views: 13
He just told me the control voltage is 57 V so I’m thinking the transfer they hooked up the control transformer wrong. They didn’t put it right terminal.
 