Re: "SHY" What is it?
I think this is the section he's refering to
680-6. Receptacles, Lighting Fixtures, Lighting Outlets, Switching Devices, and Ceiling-Suspended (Paddle) Fans
(a) Receptacles.
1. A receptacle(s) that provides power for a water-pump motor(s) for, or other loads directly related to the circulation and sanitation system, a permanently installed pool or fountain, as permitted in Section 680-7, shall be permitted between 5 ft and 10 ft (1.52 m and 3.05 m) from the inside walls of the pool or fountain, and, where so located, shall be single and of the locking and grounding types and shall be protected by a ground-fault circuit interrupter(s).
Other receptacles on the property shall be located at least 10 ft (3.05 m) from the inside walls of a pool or fountain.
But I don't have a clue as to what SHY stands for as it is not in the "99" code book any where.