Quick question that's been bothering me, had to install a 30 amp single pole GFCI Siemens breaker the other day, the white pigtail coming off it was a #12 solid. How or why do you suppose Siemens gets away with that on a 30 amp? Suppose they figure the return on the neutral will never see 30 amps? And even if it does that short piece of #12 can handle 30? By contrast I had to install a 30 amp single pole GFCI in a SqD QO panel, and that had a #10 stranded wire attached to it. Just seems sketchy to me and I just don't get why skimp on something like that.
 

AC\DC

Senior Member
Location
Florence,Oregon,Lane
Occupation
EC
Maybe they justify it because a 12 can carry a lot more than the 20 we are allowed to use.
Put 90% connection at both ends of the wire and we can put on a 30 amp breaker

Also they are the manufacturer and have alot more playroom then we do
 

Sberry

Senior Member
Location
Brethren, MI
Occupation
farmer electrician
I was having a brain fart, it is a different type of wire with current rating different than building wire and limited distance.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Maybe there is some reason they can get away with using the 90C rating of the conductors.

Or maybe someone goofed at the factory.

Jon
 

User Name

Senior Member
Location
USA
Occupation
Electrician
Hey got a call back from Siemen's, just wanted to get clarification if this was right or factory defective...basically he said its right, and because they are a manufacturer they don't have to follow the NEC, all they have to do is pass UL and they can do anything they want. I'm like wow, I suppose saving a nickel on using #12 instead of #10 adds up when you do a million of them.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Quick question that's been bothering me, had to install a 30 amp single pole GFCI Siemens breaker the other day, the white pigtail coming off it was a #12 solid. How or why do you suppose Siemens gets away with that on a 30 amp? Suppose they figure the return on the neutral will never see 30 amps? And even if it does that short piece of #12 can handle 30? By contrast I had to install a 30 amp single pole GFCI in a SqD QO panel, and that had a #10 stranded wire attached to it. Just seems sketchy to me and I just don't get why skimp on something like that.
It is time to stop applying NEC installer requirements to products tested and listed to manufacturing standards. This is what 110.3 is all about.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I suppose saving a nickel on using #12 instead of #10 adds up when you do a million of them.
Yep, $50,000. However I doubt they sell 1 million 30A 1 pole GFCIs per year though. 15 or 20A absolutely, but above that, it was pretty sparse sales volume as I recall (it's been almost 20 years now, I killed a lot of those brain cells...). Also, the savings would likely be less than a nickel per unit. But still it was likely 10s of thousands over time.

Someone might have received a percentage of that cost savings for coming up with that. When I was at Siemens if you came up with a cost savings measure, I think it was that you got a one-time bonus of up to 20% of the first year's savings. I knew someone at a factory in Juarez Mexico that got a bonus like that, I think it was $30k! I remember that he bought a huge motorhome with it.
 

User Name

Senior Member
Location
USA
Occupation
Electrician
It is time to stop applying NEC installer requirements to products tested and listed to manufacturing standards. This is what 110.3 is all about.
Normally I wouldn't buck it, but when square D does their breakers with a #10, and the amount of defective stuff I've seen in the last couple years...just being cautious. If it's OK then it's ok.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Sq. D likely uses #10 so that they avoid getting the calls or returns for having #12, which would eat into the little bit of savings you might gain. I've made decisions like that in my design days.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Normally I wouldn't buck it, but when square D does their breakers with a #10, and the amount of defective stuff I've seen in the last couple years...just being cautious. If it's OK then it's ok.
Testing and listing standards have nothing to do with product quality.
My point is the NEC requirements are very conservative because they are primarily theoretical rather than proven through third party testing.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Sq. D likely uses #10 so that they avoid getting the calls or returns for having #12, which would eat into the little bit of savings you might gain. I've made decisions like that in my design days.
Yeah, just think how answering this question this one time eats into profits.
 