chris kennedy
 - Miami Fla.
 - 60 yr old tool twisting electrician
I noticed a lug rotate while torquing a neutral. Today I went in early and took the neutral buss apart. This is an 800A P4 MDP.
In this picture note the 4/0 with the two rings of white tape entering the lug from the left side. This lug rotated while being torqued to 41?ft/lbs.
In this picture you can see how the lug rotated back upon breaking it loose.
Here is the factory installation of the lug in slotted holes in the buss.
I installed the lug in the round holes in the middle of the buss. Problem solved, right?
Nope, slight rotation on torquing, yet the new install feels super tight.
Am I over reacting to this? I have used Siemens gear for years and this is the first time I have seen this.
Thank you.
Thank you.