Idk they have plug on now too.
PoN is marketing gimmick that won't last.

I fix load centers full of debris, moisture, and corrosion, by re-terminating connections & cleaning.

The only reason certain sections of busbars last, is because they are covered by the breaker.

As soon as than PoN rail corrodes the entire load center will be junk.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I'll disagree. The PON fits very tight on the neutral rail. Using ramsy's logic of the breaker covering the bus, the breaker also covers the neutral rail.
They fit so tight, it's often difficult to install the breaker. If you have that much moisture and corrosion, you have deeper problems.
 

ramsy

NoFixNoPay Electric
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
I don't see why the PoN neutral connection is any more susceptible to damage/failure than the line side buss to breaker connection.
With no load, PoN is probably not susceptible to burn damage, like bus stabs with patina.

Time will tell how long ~5 Volt PoN connections last outdoors.

However, the Integrated circuits fed from same PoN rail, may be more frequently destroyed by surges.
 