wasasparky
Senior Member
I am an EE and former master electrician.
I am going to take my test to become a master once again.
Have any jurisdictions (or schools? IBEW? etc,) ever taken a look at the accuracy (precision) of their answers?
Two things have made me start this thread:
1. A "recent" thread here about the size of capacitor conductors for motors. (and the precision of the answers)
2. Going through the study material available from the state (MN), I am alarmed at the precision of many of their answers.
For Example: (going from memory, not what is exactly in the guide)
75kVA
208V
Z=1.2%
Available Fault Current answer was 17,348 amps. (Book I think was 17,333)
The 75 kVA I believe would be seen as "nominal"?, so would not necessarily limit the precision of the answer? (been a while since I reviewed significant digit rules)
For sure the 1.2 limits us to TWO significant digits, so the answer should be 17,000 amps...
I am going to take my test to become a master once again.
Have any jurisdictions (or schools? IBEW? etc,) ever taken a look at the accuracy (precision) of their answers?
Two things have made me start this thread:
1. A "recent" thread here about the size of capacitor conductors for motors. (and the precision of the answers)
2. Going through the study material available from the state (MN), I am alarmed at the precision of many of their answers.
For Example: (going from memory, not what is exactly in the guide)
75kVA
208V
Z=1.2%
Available Fault Current answer was 17,348 amps. (Book I think was 17,333)
The 75 kVA I believe would be seen as "nominal"?, so would not necessarily limit the precision of the answer? (been a while since I reviewed significant digit rules)
For sure the 1.2 limits us to TWO significant digits, so the answer should be 17,000 amps...