I am sizing the circuit breaker protection a sump pump motor which is 240v, 1-phase, 2-pole with 22 FLA.
Calculated so;
22A x 2.5 (per 430-52) = 55A
Chosen next size higher for standard..: 60A,2-pole circuit breaker , inverse time breaker.
Question is;
branch circuit feeding this motor should be based on 22A x 1.25%=27.5" rule , # 10 cu wire or,
#6 cu wire based on breaker size which is 60A now.???