I have a 30 HP, 3 Phase, 208V motor that I am sizing the SC/GFP device for. As I calculated and look at 430.52 (C)(1) I am a little confused.
Motor FLC = 88
88 X 1.75 (Dual element fuse) = 154A 150A or 175A protection?
88 X 2.5 (Inverse time breaker) = 220A 200A or 225A protection?
It's 430.52 (C)(1) exception no. 1 that has me questioning. It says that when the value does not correspond to the standard values that using the next higher rating is permitted. Does that mean you have to use the next higher? Should you use the next higher?
Motor FLC = 88