We pulled 2 runs today using SimPull conductors from Southwire. One pull was (4) 2/0 and (1)#2 through 135' of 2 inch PVC w/2 90? bends. We used no lube and it pulled easily. We did use a Greenlee Lil Tugger but for the last 6' I pulled on the conductors while 2 other guys shoved on the other end. One yank yielded 6'.
The second pull was 200' of (4) 500kcmil in 4" PVC w/2 90? and 1 45? we used a Greenlee 640 Tugger and it went well also. We were able to pull each conductor individually an additional 6' by hand to finish the pull.
I was impressed with the SimPull.
The second pull was 200' of (4) 500kcmil in 4" PVC w/2 90? and 1 45? we used a Greenlee 640 Tugger and it went well also. We were able to pull each conductor individually an additional 6' by hand to finish the pull.
I was impressed with the SimPull.