I have an application where 9 75hp 3ph AC motors will start simultaneously all being fed out of the same control panel.
I must size the control panel feeder, feeder breaker accordingly, and the service disconnect (circuit breaker) that will be integral to the control panel.
The NEC indicates to take the first motor at 125% and add the remaining motor FLA's.
I am thinking this is incorrect as taking the first motor at 125% will take into account the starting current of the largest motor, and this is correct, but the remaining 8 75HP motors will also start at the same time.
The only item I found in the code is in 430.24 (handbook note) that indicates that the
"feeder protective device of higher rating or setting is based on the simultaneous starting of two or more motors, the size of the feeder conductors is required to be increased accordingly"
I take this as the feeder shall be sized upon the starting loads of the motors and not just taking the largest at 125% and adding the FLA's of the rest.
Can someone point me to another code are that would address my concerns
Thanks
Thanks